Shelly inputs not working

  • Hi there,

    I've installed x7 2.5ers as a roller shutters but the last two are not working correctly, they behave in a funny way. They both respond to software commands but they don't through the 230v inputs, the strangest thing happens when I use my screwdriver (the one with a small light used for detecting the phase wire) on either the SW1 and SW2 because as soon as I do this test the Shelly takes it as a SW activation so the shutter starts moving.

    What is going on here? Are those two shellys defective? Am I?

    Thanks in advance.

  • The inputs are carrying approx. 115VAC, in order to allow to either pull them up to 230V, or down to zero, to activate them.

    From my point of wiew the inputs aren't pulled up, or down enough, if Push button is getting activated unless you are touching the inputs by phase checker.

    Could it be, that the switch, or Push button used, is equipped with a position light?

    If not, you would have tp check your installation.

    If yes, easiest would be to cut this lights out.