Hi!
I've recently connected a Shelly 1PM to my hot tub to be able to control it. It's connected on one phase, 230V, and according to the manual it is 16A. It has a 16A fuse in the central fuse box.
Now, when idle, meaning heating and low circulation but not fully turned on, the hot tub draws 2.8 kW according to the Shelly. When the jets are turned on, the Shelly shows 4.2kW for a second, then turns off by overpower consumption protection. 4.2kW translates to 18.3A.
My reasoning is that if the fuse never broke before, it is not really drawing more than 16A, but possibly momentary as the motors are starting. I know faintly about capacitive loads, which I guess one phase motors are, but not enough to understand if I'm making some wrong assumptions here. The Shelly is rated for 16A, but maybe should not be used with such a heavy load? I tried disabling the overpower protection, but it is still not accepting the high load.
So I guess my question is if I really should be using the 1PM for this use case, or if there is a better alternative? It is interesting to see the power draw, but more important to be able to turn on and off via timer and remotely.