  • Hi, I just arrived on the forum. I've searched through the various topics, but I can't find the solution to the problem I've encountered.

    I'm trying a Shelly Plus 1 that I configured from the application to drive a light point with physical buttons (in parallel) that bring the phase to the SW terminal (as instructions).

    Everything works correctly, by repeatedly pressing the buttons, the light turns on/off. Even from the application I can toggle on / off.

    The problem arises when pressing the buttons repeatedly more than 2 times in a short time. By doing this, Shelly Plus 1 activates the load with 3 pulses and then returns to the factory configuration (losing the network configuration and returning to the default input mode, i.e. bistable switch).

    Have you had similar experiences? Can you tell me how can I fix it?

    P.S. Someone might wonder why repeatedly press the buttons .... I assure you that if you have small children at home, this event is highly probable

    • Hilfreichste Antwort

    Welcome to the forum!

    In “settings” (gear wheel symbol), sub menue “factory reset”, you may configure the behaviour of the Shelly receiving multiple on signals during the first 60 seconds after powering up: Removing the activation will solve your issue.

    „Habt Geduld. Alle Dinge sind schwierig, bevor sie einfach werden!“ (aus Frankreich)

    „Nothing in life is to be feared, it is only to be understood.“ (Marie Curie, 1867-1934)

    „Es reicht nicht“, rief Schiller, „Gedankenfreiheit zu fordern, man muß auch denken können, sonst fordert man Gedankenlosigkeitsfreiheit und die ist die Freiheit zur Dummheit, welche wiederum die schlimmste Unfreiheit überhaupt ist!“
    (Aus „Besuch aus Weimar“ von Gert Heidenreich, Schriftsteller, *1944 in Eberswalde)

  • GISPUL 17. Mai 2023 um 09:46

    Hat einen Beitrag als hilfreichste Antwort ausgewählt.