Hi
I wonder if someone has some ideas to help?
I have a simple circuit with a Shelly Uni to measure depth of a water tank using a 2 wire 4-20mA pressure sensor.
I cannot get the ADC reading stable although the ADC is stable when measuring other things (VCC itself or a battery source).
The pressure sensor has stable current (to 0.1mA) when measured with a multimeter.
The pressure sensor shows a stable voltage (to 0.01V) across R1 with a multimeter.
The Problem: Voltages measured by the ADC are in the 4-5V range but are bouncing around by 0.5 to 1V. No two readings are the same.
I am using a 12V DC 2A power supply and it remains stable when measured with a multimeter.
My thoughts:
- ground loop? (I can't find it)
- damaged ADC on the Shelly Uni (it is new and has not had any other use).
Does the ADC have any special requirements such as pull-up resistor?
Thanks for your help.