Good morning, I would like to know if there is any type of problem in connecting a 2.5 shelly to 1 50W fluorescent light in each relay.
If there is a problem, is it recommended to use some other device?
Thank you
Good morning, I would like to know if there is any type of problem in connecting a 2.5 shelly to 1 50W fluorescent light in each relay.
If there is a problem, is it recommended to use some other device?
Thank you
It should e OK. There is a bit of inrush when it starts but the outputs are relays and should cope. 50W is only 0.2A at 230V so well within specs.
Hello rubenmlll,
WELLCOME TO THE FORUM
I cannot recommend. In general the Shellys have some problems with inductive loads. I had some problems exact with such types of lamps. One (18W) was connected to a Shelly 1PM and the other one (2x 18W) was connected to a Shelly 2.5. Very often the Shelly hangs and was not reachable anymore. Only a power off could solve the situation. And after some days the same problem occurred again.
After I exchanged all lamps by LED tubes the problem was solved. It never happens again.
Even another 1PM were a halogen lighting with a conventional transformer was connected to had the same problem. Sometimes it was not possible to switch on/off. Another time it switches the light on/off by itself.
After installing an electronic power supply even here all problems were gone. Never happens again.