Question about Shelly EM wiring

  • Hello! I would like to you use Shelly EM to monitor my apartment power consumption and I have a couple of questions.

    1. Is it possible to connect clamp BEFORE main circuit breaker? My breaker box is rather small and only way I can fit clamp is before main contactor. You can check a picture in attachments.

    2. Main breaker is 50A. Shoud I consider 50A clamp or it will be better to use 120A?

    • Offizieller Beitrag

    Hi @Tualua , welcome to the forum. :)

    I don't have an EM myself, sorry.

    Normaly, you shouldn't reach 50A in reality. Therefore, it shouldn't matter which one you take.

    With the 120A-version, you are on safe side.

    • Offizieller Beitrag

    Hello Tualua

    WELCOME TO THE FORUM

    You can put the CT-clamp before or behind your main breaker. This makes no difference. I would recommend you to use a 50A CT. As 66er already stated in real you will/should never reach the 50A. Therfore the 50A-CT is sufficient and you will have a more precise measurement if the CT is operated within the last third of the measurement range than in the first third.

    Grüße Bernd

    Mein "Smarthome":

    FHEM als "Master"(Cloud-Free :))mit 89 Shellys(1,1PM,2,2.5,4Pro,RGBW2,PlugS,Uni, alle mit Original-FW),13x Sonoff (Tasmota-FW),12x Blitzwolf/Gosund(Tasmota-FW),85x One-Wire Temp-Sensoren(16x D1-Mini mit Tasmota-FW),51x Modbus(Hutschienenzähler),31x Intertechno 433MHz(Rolladen-Aktoren),16x FBDECT(8 Heizkörperthermostate,8 Schaltsteckdosen),21x Homematic(16 Raumthermostate,3 FB-Heizungsaktoren,2 Repeater),1x Loxone MiniserverGo,etc