    Hello,

    I'm using this device in MQTT. For example, I got a message like this one:

    {'id': 0, 'a_current': 3.409, 'a_voltage': 231.2, 'a_act_power': 638.4, 'a_aprt_power': 787.6, 'a_pf': 0.84, 'a_freq': 50.0, 'b_current': 4.781, 'b_voltage': 230.6, 'b_act_power': 1008.4, 'b_aprt_power': 1101.8, 'b_pf': 0.92, 'b_freq': 50.0, 'c_current': 3.584, 'c_voltage': 232.3, 'c_act_power': 659.4, 'c_aprt_power': 831.2, 'c_pf': 0.83, 'c_freq': 50.0, 'n_current': None, 'total_current': 11.775, 'total_act_power': 2306.244, 'total_aprt_power': 2720.584, 'user_calibrated_phase': []}

    talking about phase A. I see 'a_current': 3.409, 'a_voltage': 231.2, ' and 'a_pf': 0.84,'. With these datas is easy to calculate Active and Reactive power:

    P = V * I * cos(phi) = 3.409 * 231.2 * 0.84 = 662.055
    S = V * I = 3.409 * 231.2 = 788.161

    Why, instead, the sensor give me the values 'a_act_power': 638.4 and 'a_aprt_power': 787.6 ???

    I tried with several messages and always seems to be wrong these datas. What's wrong? I'm missing something?

    Thanks for the reply

    Same issue. Ok emdata provide the sum of some energy data but what if I want the a_current, for example? There are not specific topics for each variable? Only a global topic with a JSON as answer?