    I have made progress!

    Sticking with the 19v HP laptop power supply measurements of 9v battery are accurate and steady. It may vary 0.01 of a volt.

    Going back to the 500 ohm resistor method

    I tried physically distancing the Shelly from the power supply and shielding it in a metal box and these made no difference.

    My breakthrough is in powering it with a 18v cordless drill lithium ion battery. Steady readings!! No fluctuations and behaves as it should.

    So the 2 totally different power supplies 19.5 and 12v both introduce severe noise affecting measurements but only when the pressure sensor is in circuit. BTW The sensor has always been a couple of meters away inside the tank.

    So I have a way forward. I can look further at using separate power supplies or somehow suppressing the noise. No access to an oscilloscope so guessing a bit!

    Thanks for the help!

    Thanks for the reply,

    I switched ECO mode off and reduced R1 to 500 ohms then to 250 Ohms. ADC readings are still fluctuating by 10-20%.

    I have also tried a current to voltage converter instead of the resistor method. Sometimes known as HW-685. Mine is: Generic Current-Voltage Transducer-Signal Converter 0/4-20mA to 0-3.3V5V10V : Amazon.com.au: Electronics

    With the converter I also get a stable voltage output as measured with a multimeter but the same bad results on the Shelly UNI ADC.

    I only have one pressure sensor and one shelly uni so can't swap them out.

    Next logical steps as I see them are below (they may take me a while)

    1. get a 24V and/or 36V supply (I don't have these and the e-bike battery voltage is too high)

    2. power the sensor and the shelly separately

    3. try the voltage measurement with a different ADC - I may have an ESP32 somewhere (which I will also need to power separately).

    Meanwhile I will lift the lid on the tank to check its level :)

    Thanks for your reply thgoebel.

    I don't have a 24V supply but I did just try a 19.5V DC supply with 2A output and the result is the same.

    The sensor I have is this one ....

    Water Level Sensor, 4-20mA Throw in Type Water Level Sensors, Anti Bending 0 5m Range Depth Input Liquid Level Transmitter, 6m/19.7ft, 316 Stainless Steel, with Waterproof Cable: Automotive: Amazon.com.au

    Some of the description says 24V, some 36V but also "9-36V Wide Voltage Power Supply".

    I may yet try it with the 36V battery from my e-bike.

    I reconfirmed that at the same time that the ADC of the Shelly UNI is fluctuating the multimeter is quite stable.

    I wonder if I need to add a low pass filter (resistor with cap to ground) on the input?

    I will look into that further and report back if I have any luck.

    Hi

    I wonder if someone has some ideas to help?

    I have a simple circuit with a Shelly Uni to measure depth of a water tank using a 2 wire 4-20mA pressure sensor.

    I cannot get the ADC reading stable although the ADC is stable when measuring other things (VCC itself or a battery source).

    The pressure sensor has stable current (to 0.1mA) when measured with a multimeter.

    The pressure sensor shows a stable voltage (to 0.01V) across R1 with a multimeter.

    The Problem: Voltages measured by the ADC are in the 4-5V range but are bouncing around by 0.5 to 1V. No two readings are the same.

    I am using a 12V DC 2A power supply and it remains stable when measured with a multimeter.

    My thoughts:

    - ground loop? (I can't find it)

    - damaged ADC on the Shelly Uni (it is new and has not had any other use).

    Does the ADC have any special requirements such as pull-up resistor?

    Thanks for your help.

    pasted-from-clipboard.png